I think though with a “hardwired” setup 625.43 requires a disconnecting means within sight per 110.25.
We have talked about this one a lot here in the forums. Here are the code sections I find relevant:
So first off, any EVSE on a 60 amp or LOWER circuit that is on standard 120/240v residential service or 208v three phase commercial service DOES NOT have a disconnecting means requirement. This really only kicks in above 60 amps, OR on 277v connected Wall Connectors (which are not very common and Tesla backed off on recommending them since some of the Model S and X units are sensitive to the higher voltages and might stop charging if voltage drifts too high briefly).
From Article 100 (Definitions):
So if you read the definition above NOWHERE does it state how close the disconnecting means must be and NOWHERE does it say anything about being within line of sight.
I personally think needing an ugly and expensive disconnect switch right next to Wall Connectors is silly. These are basically maintenance free devices (unlike air conditioners which is what most commonly requires disconnects like this). So if someone does come out to replace a Wall Connector, I don't see it as much of a burden to have to go turn off power at the circuit breaker. About the only thing I could think of replacing in the unit without replacing the entire unit would be the contactor.
So with that being said, I do think it is a good idea to have a "lock off" device installed on the breaker unit *especially* if the breaker is out of sight of the unit (so nobody else goes and turns it on when you are working on it). My reading is that these breaker lock off devices installed in the feeding panel cover this code requirement.
Also note that in the event of someone getting electrocuted, etc... by an EVSE I am not sure the danger is much different between a 30a 240v breaker and a 70a 240v breaker... The voltage is still there... And both are more than enough current to kill you.
And for completeness, here is 110.25. Nothing really interesting here. Just that you need to be able to show up on site to work on the EVSE and shut off the device and shove your lock through the hole. The breaker clips I describe I believe cover this.
Note though that I think certain AHJ's have either added more stringent requirements, or they are mis-interpreting the code and they have asked folks for disconnects within line of sight.