Hi All,
Apologies if this has been mentioned already, with a 32a commando socket, does anyone have PME fault detection fitted?
Thanks in advance
My current (no pun intended) understanding is if you already have a 32A commando you can use it, you can even have a commando socket installed without PME if the expressed intention is not to charge an EV, but if you want a commando socket installing with the intention of charging an EV, the regulations are more strict and (I'm no electrictian) I believe that includes PME extra fault detection. I kind of think its craze the same socket can have two different levels of protection with no obvious indication and the only difference is the expresed intention at the time of installation.
Back in the day Tesla used to pay for commando sockets to be installed and they didn't have PME fault detection fitted as the regs didn;t require it at the time. I had one installed and a few years later I swapped the commando socket for Tesla wall charger.. and still no PME fault detection. I am sure I am far from unique on this. Regs aren't generally backdated and the PME thing is relatively recent (maybe 3 years).
its a lot safer than people using extension leads out of hotel windows
I'm shocked! I'd -never- do that!Oh dear, are you looking at me?
I'd -never- do that!
Not really. More like when the local DNO has skimped on maintenance of their 50+ year-old cable plant, or some plonker with a JCB is digging down the street.The PEN protection is not for now. It's for 10 years time when the next owner has rolled over the cable lots of times with his cyber truck and still insists on using the charger in the rain. You will probably not have a problem because you are sensible and wouldn't use equipment in that state. The regs are designed to protect others who wouldn't know better.
Ah, sorry. Am I mixing it up with the other fancy RCD you are supposed to use to prevent earthing differences between things inside and outside the house?Not really. More like when the local DNO has skimped on maintenance of their 50+ year-old cable plant, or some plonker with a JCB is digging down the street.
The broken PEN problem arises entirely outside your installation, and (if it occurs) will bite you even if all your equipment is in 100% top shape (assuming that it doesn't include an open-PEN detector and does use a TN-C-S earthing system). Damaged cables within your installation don't give rise to the problem.
Ah, sorry. Am I mixing it up with the other fancy RCD you are supposed to use to prevent earthing differences between things inside and outside the house?
Possibly the most informative post on the subject ever written. Thankyou.PEN protection
The PEN conductor is used in the supply cable in the street - combining Earth and Neutral in a single wire (which you aren't allowed to do within your installation, ie. downstream of the meter earth and neutral are separate wires). This is only one of several earthing systems, but it is by far the most common in the UK. The snag is that if the PEN gets broken in the street, your neutral and earth wires - so including the chassis of your car if it's plugged in on charge - can end up at the same voltage as the live wire. So the net effect is it seems like there's a power cut - L is at 230V compared to true earth, but so is N, hence the voltage between L and N is zero. All your earth wiring is also at 230V above true earth.
If all your wiring is inside the house, then this isn't a big deal. Although all your earthed appliances are now 'live' (230V above 'true earth'), other regulations have arranged that everything else you can touch is also 'live' - everything you can touch is required to be either insulated or connected to that same earth terminal, so even if it's now a bad earth terminal, everything around you is at the same voltage, and your body can't touch two things at different voltage to get you a shock.
However, when you step outside your house your feet are now standing on, maybe damp, 'true earth' and your car's chassis is 'live'. This time you do get a shock when you touch the car. Note also that none of the conventional protective devices (RCDs etc) do anything to help you here - it's the earth connection to the car that's killing you, and conventionally earths are all permanently wired, they don't go through switches or RCDs.
The fix is either to put in one of these PEN protection units, which _does_ put a switch in the earth connection to the charging equipment and hence the car and turns it off if the mains voltage is out of spec; or else you use a different earthing system that doesn't connect earth and neutral wires - for example the 'TT' system where the earth wires in your installation are connected to a rod in the ground. There are pros and cons to both these systems.
DNOs are required by the ESQCR regulations to report each time they have a broken PEN incident, so statistics are available and a risk assessment done at the time of writing the Regulations showed that if all cars in the UK were EVs there would be around 6 deaths per year from this cause (range of probabilities from 1 every 5 years to 36 every year). The numbers in there are sufficient to convince me that it's a real problem that needs solving (indeed I think they got their methodology wrong and it's slightly worse than they say).
RCD types
RCDs work by measuring the current in the L wire and comparing it to the current in the N wire - if those currents are different, then some must have "leaked out" somewhere, indicating a fault - maybe it's leaked out through the body of a person touching the live wire and their feet on the ground.
The original type of RCD is known as "Type AC". These are easy to make with a purely electromagnetic design - no electronics. However, at the heart of the design is a transformer and so they only work with pure AC - such as you would get with a person directly touching the AC live wire. However, inside a car charger (and many, many modern devices) the AC gets rectified to DC and so a fault in the car's charger (or someone poking their finger inside) won't give a pure AC leakage current and so won't trip the RCD.
Next up is the "Type A" RCD. This uses essentially the same physical arrangement as the Type AC, with a transformer, but adds some electronics to process the signal coming out. This will respond to not only pure AC but also pulsed DC such as you might get after the rectifier in a charger (or a motor drive, or a solar inverter etc etc). Costs almost the same as the Type AC nowadays.
Top of the range is "Type B". This can detect everything that the Type A can do, but also detects pure DC leakage currents (or anything in between). Unfortunately, the transformer-style design of the other types can't do this and a much more complex circuit is needed. They are usually much more expensive and twice the physical size as a result). If money was no object, that's what you'd be fitting.
For EV charging, there's obviously a very strong argument that Type AC isn't good enough, as there are obvious failure modes (damage to the EV charger) that can give pulsed DC which a Type A will detect but a Type AC will not. The original EV charging regulations (2011/2012 as mentioned above) therefore required a minimum of Type A and disallowed Type AC.
There's not really any plausible fault scenario that could give rise to a pure DC leakage, so there's not a clear requirement for the full capabilities of Type B, but there is one further snag.
If you've got a permanent DC current flowing (maybe harmlessly) on top of the AC, then that can saturate the transformer in the Type AC/Type A RCDs and stop them detecting genuine faults that they would otherwise be able to handle. To be certified as Type A, RCDs have to keep working even in the presence of 6mA of DC current, but more than that and they are allowed to malfunction (ie. fail to save you when disaster strikes). Unfortunately, the EV charging standards (the specification for how the Type1/Type2 charging connectors work) relies on a 12mA DC current in the earth wire of the charging cable to detect that the wire isn't broken etc. Regulation-makers began to worry that the 12mA DC current could somehow turn into a 12mA leakage current and so disable any Type A/Type AC RCDs - not just in the chargepoint, but maybe elsewhere in the house. Now, it's a pretty outlandish fault scenario for the whole of that 12mA to get diverted into the L or N without the whole thing going bang, and in any case that 6mA spec on Type A devices is a minimum (real ones will typically do better), but it's still a bit unfortunate that those numbers are what they are and this is a forseeable safety risk that can't really be brushed under the carpet.
A Type B RCD would solve the whole problem, but they are desparately expensive, so the original Regulations had some ambiguous wording that let you get away without one. Then it was noted that the problem could be fixed by using a device that specifically looked for that 6mA or more of pure DC and shut down the EV charge circuit; you could then use just a Type A for the main RCD function safe in the knowledge that it won't be defeated. This extra circuit is much simpler (hence cheaper) than a Type B.
So now the regulations have been clarified, and you need a Type B unless it can be shown that >6mA DC can't occur, in which case you can use Type A as before. The >6mA detect circuit can either be built into the chargepoint, or you can get a special RCD that combines the 6mA detect circuit with a conventional Type A - one manufacturer is branding these as "Type EV" although that's not an official designation.
Personally, I think the risk here is rather lower than the PEN case and it's questionable if the extra cost over just a Type A is worth it - but I don't have any proper statistics to prove that, and I have upgrade my own chargpoint installation to have a "Type EV" RCD.
Indeed… @arg makes infrequent, but always excellent, contributions these days.Possibly the most informative post on the subject ever written. Thankyou.
I have upgraded my own chargpoint installation to have a "Type EV" RCD.
I’ve been charging with a 32A commando for more than four years.
Doepke are the ones pushing "Type EV".I'd like to do the same (hope you are on commission!). Can you point me to a brand / model pls, so I can ask my sparky to do that (i.e. so he will know what I am trying to tell him!)
There's no such thing as "safe". The only way to avoid the risks associated with EVs is not to have a car - but then you might get run down by a bus. So it's all about relative levels of risk.I’ve been charging with a 32A commando for more than four years. I decided on this option as I wasn’t eligible for the £500 OLEV grant. I installed it myself and just got an electrician to wire it into the consumer unit and check I’d done it properly. it’s been 100% reliable and saved me a lot of money.
It doesn’t conform to current regs so it would be irresponsible of me to recommend that anyone else does this. But I’m satisfied it’s safe, and it’s every bit as safe as a 3 pin UMC.
That means you don't need PME fault protection - you aren't using the PME earth.Actually, now I think about it ... I have an earthing rod on my wall connector. Perhaps I don't need to upgrade anything to "better"?
I've asked my DNO to upgrade my main fuse from 60A to 100A when I installed it, so surely if they're not too stupid, they register the new Amp usage rather than what's behind it?One thing I don't think has been mentioned in this thread, is that you need to inform the DNO that you are fitting a 32A charger, so that they can keep track on how their network is being loaded. If a lot of people start fitting and using DIY 32A commando sockets there might be some unintended consequences...
These are two different things. Your new fuse allows you a higher instantaneous demand. The thing they are concerned about is long-duration demand: your EV charging may well have fitted within your existing 60A fuse, but could still cause them problems.I've asked my DNO to upgrade my main fuse from 60A to 100A when I installed it, so surely if they're not too stupid, they register the new Amp usage rather than what's behind it?