Hi everyone who is following this particular post. I have specifically joined this group to provide the following response (though I have not read all previous responses)
I am an electrician and am currently installing one of these chargers. I wanted to provide a response as an electrician with an interpretation and reasoning. I am NOT providing technical guidance, and will NOT respond to questions, your installer must use their own skills to sign off on their own installation. I am trying to assist owners to understand their requirements.
The new rule book AS/NZS 3000:2018 is a little vague in some areas surrounding EVs. The previous rule book (AS/NZS 3000:2007 - didn't have a specific clauses, but they were also implied). In the current rule book, appendix P provides guidance on installation techniques, but is vague with isolation requirements. Other sections of the rule book are specific though, but they don't necessarily specify EV in context.
However, having spent an hour going over different clauses, I have contacted NECA, whose current tech advisor is an ex electrical energy inspector. We have reviewed all clauses that may relate to the installation of charging stations and both agree that an isolator must be installed for compliance - and safety.
Some things to reflect on are (these are compliance requirements):
* Socket outlets (of any size and type) must be fitted with an isolator. A charging station has a plug and socket.
* Energy converters (i.e. chargine stations converting AC to DC), must be fitted with an isolator. The charging station is an energy converter, converting AC to DC for charging purposes. If we consider solar, battery storatge requires an isolator for the battieries and the inverter.
* Appliances (yes this is an appliance) must be fitted with an isolator.
* Isolators must be installed in a location where there is direct line of sight and accessible at all times to isolate the appliance, socket outlet, or energy converter.
... there are no doubt other clauses as well.
If we consider this from a safety perspective.
* There are complex electronics that control the charging of EVs. Both the charger and EVs are expensive. Should a fault occur you would want to isolate the charger and EV within a short time frame.
* Should the device start to malfunction, you would want to isolate the device within a short time frame.
* Sometimes RCD/RCBOs (circuit breakers with residual current detection) don't work satisfactorily. Where a fault occurs, you need to islate the device quickly.
* Inverters fail, fires occur.... etc etc.
Summary
Whether you do or don't want an isolator, or have or have not got one currently fitted.
They are a mandatory item specified in AS/NZS 3000:2018 and previous rule books (though vague - they are implied), required for the safety of you equipment and EV.
I hope that helps owners with their choices.
Best wishes,
Greg.