Thanks for your replies @Gauss Guzzler @Sophias_dad and @3sr+buyer , I've decided to have a completely different company come out and rewire the current circuit and change to a 50 amp breaker, inspect the sub panel to make sure he wired that correctly as well, and then run another circuit to hardwire the wall connector as it should be.
Just wanted to jump in and update this. Had another electrician come out to take a look at my situation. Turns out what I thought was a 60 amp breaker on the welder circuit is really a 30 amp breaker. There are 2 30 amp breakers linked together, which led me to believe is was 60 amps. So that circuit is good. The circuit to power the 60 gal air compressor is good and the wires used to power the subpanel are good. He said he would add a new 60 amp circuit with 6 awg wire to power the wall connector and would also put in a 90 amp breaker feeding the subpanel just incase I ever weld while the car is plugged in. So now all I gotta do is wait for the wall connector to show up and he'll come back out to do the install. I ordered the wall connector on the June 25 so hopefully I'll get it soon, still haven't received any shipping info....