So there is no home supercharger. What you're probably thinking about is the wall charger. The wall charger is slightly faster than a NEMA 14-50 outlet, and looks nicer, but is not normally worth the cost. I've had my 3 for 1.5 years and only use a NEMA 14-50. If you go that route, no need to upgrade unless it's for aesthetics.
Nema 14-50 will get you ~29 miles an hour. Wallcharger will get you somewhere around 42 miles an hour if you get 60 amps.
Since you're being pedantic, there is no wall charger either.So there is no home supercharger. What you're probably thinking about is the wall charger. The wall charger is slightly faster than a NEMA 14-50 outlet, and looks nicer, but is not normally worth the cost. I've had my 3 for 1.5 years and only use a NEMA 14-50. If you go that route, no need to upgrade unless it's for aesthetics.
Nema 14-50 will get you ~29 miles an hour. Wallcharger will get you somewhere around 42 miles an hour if you get 60 amps.
No. A 14-50 is wired with a 50A breaker and corresponding wiring which meets the electrical code for a 14-50. To go to 60A for a Wall Connector requires different wiring, not just changing the breaker.So as long as I wire the NEMA 14-50 to a 60 amp fuse I could theoretically add a wall charger later if I want it to?
So as long as I wire the NEMA 14-50 to a 60 amp fuse I could theoretically add a wall charger later if I want it to?
You can save a little using a 6-50 instead of a 14-50. Neither the mobile connector nor the HPWC needs a neutral wire.
I ran 4/3 gauge copper to both my HPWC and an additional 14-50 (for future). If I was doing it again, I would have used 4/2 and a 6-50.)
If you are considering swapping an outlet for a Tesla HPWC in the future, there is an important step you must take. You'll need about 6" more wire for the HPWC, so make sure you keep some extra wire in the wall that you can pull out later.
NM wire has a 60C temperature rating. 6 gauge is rated for 55 amps, 4 gauge is rated for 70. For the HPWC to provide 48 amps continuously, you need a circuit that has 48/0.8=60 amp capacity.
There is apparently an exception in the code allowing a 60 amp breaker on a 55 amp wire, but when buying the wire for this purpose, I'd just get one rated for this load.
I think 625.41 makes the case that the conductor must be able to handle 125% of the continuous load and there is no “round up” rule like there is for breakers. Since the 6/3 Romex ampacity limit is 55A, the maximum current allowed would be 44A. Therefore, if one installs the Wall Connector they cannot use it at its rated capacity of 48A. Not sure that manually configuring it to run at a lower current would meet the code. It seems like it would be a better idea to just use the right wire for the ultimate application rather than try to justify changes after the fact.So apparently (unless there's something else hidden in the code) you can use 6/3 NM wire with a 50 A breaker for a 14-50 now, and later replace the 14-50 with a direct-wired HPWC and change the breaker to 60 A.
So if you do this then update to the HPWC later, you’ll have to change the breaker - the Gen-3 HPWC has GFCI built in and won’t work right with a GFCI breaker. Likely not a big deal, but something to remember.However: If your jurisdiction uses the latest (2020) version of the NEC, or you want to meet it because safer is better, a 14-50 in a garage requires a Ground Fault Circuit Interrupter. This may be true in the 2017 code too; I forget when it changed. And a 50 A GFCI is $100, vs. about $10 for a regular breaker.
Don't the length between the plug and the circuit breaker needs also to be evaluated when determining wires type?I think 625.41 makes the case that the conductor must be able to handle 125% of the continuous load and there is no “round up” rule like there is for breakers. Since the 6/3 Romex ampacity limit is 55A, the maximum current allowed would be 44A. Therefore, if one installs the Wall Connector they cannot use it at its rated capacity of 48A. Not sure that manually configuring it to run at a lower current would meet the code. It seems like it would be a better idea to just use the right wire for the ultimate application rather than try to justify changes after the fact.
Don't the length between the plug and the circuit breaker needs also to be evaluated when determining wires type?
I think 625.41 makes the case that the conductor must be able to handle 125% of the continuous load and there is no “round up” rule like there is for breakers. Since the 6/3 Romex ampacity limit is 55A, the maximum current allowed would be 44A. Therefore, if one installs the Wall Connector they cannot use it at its rated capacity of 48A. Not sure that manually configuring it to run at a lower current would meet the code. It seems like it would be a better idea to just use the right wire for the ultimate application rather than try to justify changes after the fact.
Don't the length between the plug and the circuit breaker needs also to be evaluated when determining wires type?