I’m all for having the outlet wired correctly, but help me understand the benefit of replacing the 6-50 with a 14-50. Compatibility for his UMC when traveling? Otherwise I don’t see a benefit for him when charging at home.
You can install our site as a web app on your iOS device by utilizing the Add to Home Screen feature in Safari. Please see this thread for more details on this.
Note: This feature may not be available in some browsers.
Not a big deal. The ground and neutral are bonded together in the panel anyway. If it makes you feel better cover the white wire with green tape and wallah, you’re code compliant.It is mis-wired. The white (neutral) wire should NOT be connected on a 6-50. The green safety ground should be used instead. Since you have all four wires, I'd recommend replacing the 6-50 with a 14-50.
Not a big deal. The ground and neutral are bonded together in the panel anyway. If it makes you feel better cover the white wire with green tape and wallah, you’re code compliant.
I’m all for having the outlet wired correctly, but help me understand the benefit of replacing the 6-50 with a 14-50. Compatibility for his UMC when traveling? Otherwise I don’t see a benefit for him when charging at home.
Not a big deal. The ground and neutral are bonded together in the panel anyway.
They are required to be bonded together at the main entrance panel - where the meter is. They are NOT bonded together in a sub-panel. So in the case of a sub-panel, the neutral may very well have a different potential from the safety ground out at the receptacle.
Whether you are allowed to or not depends on the wire type and thickness. Here is a chart about that, which I can explain a bit.Now just want to think if I should change out the breaker to a 50 amp vs. the current 40 amp.
...except you can't put a 60A breaker on a 50A outlet. That would only be if they move to an HPWC.For the second column, that is if they are separate wires run in a plastic or metal conduit. That would not be inside your wall, so you will see if that is running along the surface of the walls on the outside. That kind of installation can dissipate heat better, so you'll see the 8 gauge rated for 50A, and the 6 gauge rated for 65A. So if it's that, it's likely you can do the 60A breaker.
In the "option 1" scenario, if the outlet is connected to a sub-panel, one would also need to change the connection in the panel from the neutral bar to the ground bar.The way that is wired is a little bit out of code, but not a big deal to fix. It is supposed to be the green or bare copper wire used for the ground on the 6-50. White is always supposed to be reserved for neutral unless you have no other choice, and then code does allow you to mark the white wire green to show that it's repurposed as a ground. So yeah, you have a couple of easy choices:
1. Keep the 6-50 outlet but remark that white wire.
2. Change it to a 14-50 and use all four wires.
And then buy whatever adapter for the outlet you have.
Then there is a safety issue with the sub panel. The neutral should always have the same potential as ground. The sub panel neutral would only have a different potential from ground if the ground and neutral weren’t bonded properly at the service panel, or it was on the load side of a transformer and the transformer was bonded incorrectly. In those two cases, it would be unlikely that the ground wire would provide a low resistance path the ground anyway.
Oh, whoops, you are totally right. I know that, but my brain shifted gears halfway through this when just looking at the wire capabilities, and I forgot about the outlet still being on there. Yes, with either a 6-50 or a 14-50, it still can't go higher than a 50A breaker....except you can't put a 60A breaker on a 50A outlet. That would only be if they move to an HPWC.
Then there is a safety issue with the sub panel. The neutral should always have the same potential as ground.
Yeah, I hadn't even gone into why that was wrong before, but thank you. Neutral carries current throughout the house from the 120V circuits, and ground doesn't (shouldn't, unless something is wrong). So that would not be unusual for the neutral to have its voltage pulled a bit away from 0V, while ground should always be pretty solidly there, so they can have a little bit of voltage difference. The bonding at the panel should be holding them close, but at the ends of some wire runs, there will be a little bit.Um - no. I could go into a long explanation, but besides the National Electrical Code, there are already countless web pages and youtube videos on the topic. Here are a couple to get started:
the neutral will not carry current in an outlet for an EV...Oh, whoops, you are totally right. I know that, but my brain shifted gears halfway through this when just looking at the wire capabilities, and I forgot about the outlet still being on there. Yes, with either a 6-50 or a 14-50, it still can't go higher than a 50A breaker.
Yeah, I hadn't even gone into why that was wrong before, but thank you. Neutral carries current throughout the house from the 120V circuits, and ground doesn't (shouldn't, unless something is wrong). So that would not be unusual for the neutral to have its voltage pulled a bit away from 0V, while ground should always be pretty solidly there, so they can have a little bit of voltage difference. The bonding at the panel should be holding them close, but at the ends of some wire runs, there will be a little bit.
Um - no. I could go into a long explanation, but besides the National Electrical Code, there are already countless web pages and youtube videos on the topic. Here are a couple to get started:
Subpanels: when the grounds and neutrals should be separated — Structure Tech Home Inspections
Why separate the ground bar from the neutral bar in a sub-panel? - E&S Grounding Solutions
You're right, but so what? The outlet has to be wired per code regulations, without regard to what gets plugged in and how that appliance makes use of the power available to it.I’m not arguing with you about that. Sub panels should have isolated grounds and neutrals, so what?
My point is that at the EV outlet the potential between ground and that “white colored wire” identified as a neutral but carrying no current will be zero, assuming everything else is connected right.
Sigh. You are not following the conversation. Yes, the neutral is unused in that particular outlet.the neutral will not carry current in an outlet for an EV...
And we were correcting you on this, that in a subpanel, the neutral can have a little bit different potential from ground, because if that subpanel is feeding a few circuits, including some 120V ones, it can be carrying current on the neutral and can have some different potential at that point.Then there is a safety issue with the sub panel. The neutral should always have the same potential as ground.
Yes, what you have planned sounds good and should be code compliant.We will test a friends mobile charger when he returns. I will also check the gauge of the wire. We will only charge at 32 amps and leave the breaker at 40 amps.
In the event we need to change anything, we would do that the correct way. The outlet is 24 inches from the pannel.
No, it doesn't have to be. NEC allows for this for 40A circuits. There is no 40A outlet type, so what other outlet would one put on a 40A circuit? Ovens do this really frequently, and it's an exception specifically written into the electric code to put a 14-50 or 6-50 onto a 40A rated circuit, using wire and breaker appropriate for a 40A circuit.If you install a 14-50 which is a 50A outlet, Per code I think you must install wire and breaker for 50A. This is so someone does not come along and plug a 50A load into the 50A socket and think its OK.
So I would buy a 50A breaker and 6 ga wire. The ground wire can be 8 ga.