A couple of weeks ago I asked my installer to quote me for a second Powerwall. He said in his experience our DNO is likely to refuse permission.
I then asked him what the situation would be with the DNO if I got a 3 phase supply into the house. He responded that it would be approved but that we would then need 3 powerwalls at the property, one for each phase? I think that is wrong, does anyone here have experience of such an eventuality?
Yeah, I think they're wrong... this is what we did below... so it can be done.
Our house used to be on a standard Single Phase supply, going into a Single phase meter. Through to a Single Phase Consumer Unit.
Our two Powerwalls powered the house on this Single Phase, and backs it all up through the Tesla Gateway 2. So we had no problems with two Powerwalls on a Single phase supply.
Now we have a replacement 3 Phase supply, going into a 3 Phase meter, and then into a 3 Phase distribution board.
But... we've kept the house on Single Phase, and the Single Phase Consumer Unit. No need to change because there's no high loading inside the house.
However, we now have access to this new 3 Phase distribution board and can attach things to that... like a 3 Phase 22kW Ev Charger as an example.
No idea why you would need 3 Powerwalls on each Phase... sounds completely over the top? ... if your house isn't already loaded with 3 Phase appliances and needs that capacity
Our two Powerwalls continue to provide the house with full backup on Single Phase... and we charge the car on 3 Phase.