Did you mean to write "something else" instead of "nothing else"? I think the opposite is true. I think most Tesla owners use a 240 volt NEMA outlet or a hard-wired EVSE, both or which would be considered a Level 2 charging option. I always thought Level 1 was 120 volts AC and Level 2 was 208-240 volts AC. Level 3 is high voltage DC.
Well that appears to be true. Majority of Tesla users have NEMA 14-50 portable Tesla EVSE or hard-wired EVSE.
Where did you find that Level 2 needed to be hard-wired?
With the socket limitation (NEMA 14-50 should be the most powerful?) Level 2 EVSE-s could be plugged into a socket and not hard wired. With Tesla's portable EVSE it's fine, AFAIK adapter limits the maximum current (and portable EVSE is already limited anyway). But some people are "sneaky" and wire a NEMA 14-50 plug to the stationary EVSE with higher input power limit (80A in US?). Making EVSE portable (can be unplugged) and usable on any NEMA 14-50 socket. Just to avoid permits. Which results EVSE dropping to Mode2. This mode should be used occasionally with care. In the long run it might end up problematic.
People are people - if something could be done wrong SOME people will do it. For example 0.1% is realistic expectation. Hundreds of potential house fires annually.
If US continues with NEMA 14-50 at 40A, there will be people who disconnect incorrectly. Starting from the NEMA side.This will result in arcing. And this will degrade the coupling. Which will end with fire eventually. That is not a huge problem with Level 1 (both US and EU) due to low amp limit.
Tesla's EVSE might have a temp sensor in the NEMA adapters, not sure. Not all EVSEs are from Tesla.
This is why Mode 3 should be mandatory for daily use. No contact degradation, no arcing. STOP command before disconnection.
I don't think we usually talk about the car end in European Tesla circles either. All Tesla cars...
Exactly. All Tesla cars. But not all EV's. Leafs use Type1 MY 2010-2017. Like I said, the problem will be solved soon.
There are more complex reasons why Mode 2 should be avoided (worldwide, in EU Mode 2 is now the minimum requirement, Mode 1 is banned for EVs). The cable between EVSE (device that monitors safety and integrity of the connection) is not monitored well enough. This includes 5 highly loaded pairs of junctions between:
a) circuit breaker to wires b) wires to socket female pins c) female pins to male pins d) plug male pins to wires e) wires to EVSE internal terminal. In addition cable between plug and EVSE can (and likely it will) be stressed. Therefore it must be stranded. This can also be ignored by some electricians as EVSE appears to be installed permanently. This cable might increase in resistance over time due to mechanical stress. Also that part of the cable is not limited in length. And extensions can be used.
And cable between junction box and EVSE is not protected (one can be electrocuted). But cable between EVSE and vehicle is protected with RCCB. Not possible to die, literally. Only by strangling around the neck or something like that.
Mode 3 requires direct connection between circuit breaker and EVSE internal terminals. Also cable must be immobilized and protected in some scenarios. This is much safer. This is why Mode 2 should be avoided (seriously) at Level 2, especially above 20-25A. This is why Mode 2 is fine with Level 1.
I had my thesis about home EVSE's, l could keep the topic open for 10 more pages
Though I have lots to learn about US.