It is an EU TWC.Are you referring to EU TWC?
Self-Monitoring and Recovery
The Wall Connector has a ground monitoring
circuit that continuously checks for the
presence of a safe ground connection and
automatically recovers from faults. Manual
testing and resetting is not required.
Temporary problems such as ground faults or
utility power surges are overcome
automatically. If a residual current fault occurs
that interrupts charging, the Wall Connector
automatically tries to clear the fault and re-
attempt charging.
The problem is thatTesla do not give any details so its not possible to say if the protection is for the TWC or for the user...
Are you charging on 230v 32A single phase? (7.36kw)?My previous ones were separate but faulty so they've just changed it to this combined unit.
Is this combined one to the correct standard? Just wanted to check please
The issue is not so much protection of the TWC, its more to do with DC leakage 'blinding' a Type A or A/C RCD that is protecting other circuits. It doesn't take much DC leakage (6mA is the limit for UK device protection) to affect the protection of other circuits supposedly being protected. So a fault elsewhere in the house may not be protected against. The Type B, or an alternative 6mA DC protection device will prevent this blinding.
Yes max 32A single phase cheers.Are you charging on 230v 32A single phase? (7.36kw)?
Ah I see.Yes max 32A single phase cheers.
It's UK domestic so sometimes goes up to 240v but usually I get about 235V
My previous ones were separate but faulty so they've just changed it to this combined unit.
Is this combined one to the correct standard? Just wanted to check please.
max 32A single phase
It's UK domestic so sometimes goes up to 240v but usually I get about 235V
Doesn't say type B anywhere though?
Wall Connector features built-in RCD Type A + DC 6mA.
After reading most of this topic, I'm still trying to figure this out..I've read the whole topic but I couldn't really come to a conclusion..
Type B is the new standard. Type A used to be OK.
Now, I bought a Tesla wall charger, 3x32A.
I am going to get it installed. No standard requirements in the country it will be installed.
And no certified / experienced installers.
Would I be risking my family's life, our house, if I use a TYPE A instead of TYPE B 3x40A RCD?
It’s the regulations that ensure you have the elements that will keep you safe. There is also certification to be supplied to your DNO. From what you say I suspect that you will require either an earth rod or O-pen device such as the Matt:e. An appropriately qualified installer will tell you which is required for your situation.Can anybody give a clear answer what else do I need for my 3x32A Gen3 TWC install? I just need to be safe, I don't care about regulation.
Do they have the concept of a DNO in Serbia / I’ve not the slightest clue. Not even sure why this is being asked in a UK sub-forum. Clearly the person need to comply with their local electrical regulations. Messing about with EV charge setups by unqualified people is just asking for trouble.It’s the regulations that ensure you have the elements that will keep you safe. There is also certification to be supplied to your DNO. From what you say I suspect that you will require either an earth rod or O-pen device such as the Matt:e. An appropriately qualified installer will tell you which is required for your situation.
Good point! I wasn't paying attention to OP location.Do they have the concept of a DNO in Serbia / I’ve not the slightest clue. Not even sure why this is being asked in a UK sub-forum. Clearly the person need to comply with their local electrical regulations. Messing about with EV charge setups by unqualified people is just asking for trouble.
Looks fairly comprehensive. Under-voltage release + over current protection + residual current protection. As Adopado said that doesn’t cover your ground/earth arrangement- see page 10 of the TWC manual.After reading most of this topic, I'm still trying to figure this out..
Tesla states "Wall Connector features built-in RCD Type A + DC 6mA."
Can anybody give a clear answer what else do I need for my 3x32A Gen3 TWC install? I just need to be safe, I don't care about regulation.
I've seen some local installers use circuit boxes like this for other brand chargers, but I'm not sure If I need all of this stuff for TWC, or they're just trying to sell more equipment than needed.. Also I'm not electrician so I'm not sure what most of this stuff is:
View attachment 926656