Add me to the group of people that are experiencing Charge Reduction with absolutely no issues with the premises. Sort of, I shall explain.
My home, is on a highly over-loaded (Or at least, over-subscribed) transformer being shared with at least 7 homes. I'm only one with a EV. Winter, almost no Electric Loads from other homes, Summer, AC loads nail that transformer.
Now, HPWC is 1 ft from breaker box. HPWC connected to 100 amp breaker by 2AWG (Larger then specified by Tesla). Breaker box is 5 ft from meter, fed by 2/0. More then large enough for my 200 amp service.
Meter being fed by transformer by 2/0. Though, transformer is far away.
Voltage Sag. Start at about 240v at no load, at about 40 amp load, drops to about 230v, at 80 amp load, drops to about 222v. At my home, the car will stay at 80 Amps for about 5-10 minutes before reducing to 60 amps. Despite the voltage drop.
Now, at my parents motel, they have a 70kW transformer.
During the summer, that 70kW transformer is feeding their motel, and 2 houses. So 4x200 amp services and 2x100 amp services. During the summer, the transformer is really loaded, but utility wont upgrade it as it is handling the load.
Now, the HPWC currently online (Had to remove the second one, as we ran out of available service without adding a second meter. I am working to resolve this by swapping loads between breaker panels and meters for the motel).
That HPWC, is located on the garage of the "Beach House". It is fed by one of the 200 amp services, and has that all to itself.
HPWC is 12ft from garage breaker panel, fed by 2awg. Garage panel fed from main panel by 2/0 Aluminum at ~13ft run. House Fed by 2/0 Copper.
During the winter, with the Motel Closed, the total load on the 70kW transformer is about 10kW. Thats factoring in the main house, 2 houses across the street, and misalenous loads. Either way, it's next to nothing considering the transformers size.
Voltage at the HPWC is STRONG. Start off at about 245v. At 40 amps, about 238v, at 80 amps, about 235v. So MUCH MUCH MUCH less voltage drop then my home.
The car will stay at 80 amp for a maximum of 30 seconds before backing down to 60, despite the much less voltage drop.
In the second instance, at the motel, I have had the utility out, checked all the lines, transformer to the house etc... noting wrong, wiring proper size, tight connections etc...
Now, one other note, before removing (temporally until i get the load situation resolved) the second HPWC, I gave er a good test. Now, this second HPWC, was literally next to the breaker box, that was 2 ft from the meter, that is connected with 2/0 directly to the transformer. So a total wire run with oversized wiring, from HPWC to the Transformer, was less then 25Ft. I'd gather thats considered really dang close.
Same result when charging at 80 amps. about 30 seconds and it was already backed down to 60 amps. This test was done once season was over, and motel closed, so all large loads were gone (motel portion is completely electric, the houses use gas for heat, so no real loads from the houses).
Voltage drop measured: ~248 no load, ~242 at 40 amps, Fluctuating between 239 and 240v at 80 amp load. So extremely little voltage fluctuation.
Still, drop from 80 to 60 amps. Makes no sense. It will sustain 60 amps all day, but doesnt like 80 amps. Utility put some sort of line monitor. They were a little vague on the details of it, but it was to test for "Noisy" power and "hickups" is how the utility worker said it. I might also mention, the 10 megawatt hydro plant is 2 miles away.
No explanation as to why it happens.
in fact, the ONLY, and I will repeat, ABSOLUTELY ONLY HPWC IVE EVER CHARGED AT THAT I DID NOT GET CURRENT LIMITED WAS AT Marshall Auto Body. Shout out to Scott for his awesome setup.
He has a 80 amp HPWC, a I believe 70 amp J1772 Clipper Creek, 70kW Solar Array, and is in the process of completing a CHAdeMo install at his body shop.
I will need to take that statement back, the HPWC's at the Highland Park service center I did not get current limited. But in terms of Non-Tesla owned HPWC's, EVERY other HPWC or 80 amp charging location I've visited (And it's A LOT) other then Marshall Auto Body has gotten current limited at some point to 60 amps during the charge session.
Please don't take this as a argument. I'm voicing my findings in this thread, as I'd like to find a solution to this issue. I will also add, I have a retrofit dual charger. My car was shipped with single charger. At time of retrofit, my master was also replaced as it would not communicate with the slave. I have had duallies for exactly 1 year now.
- - - Updated - - -
You went through 8 UMCs in a year, and I am still on my first UMC after 20 months of charging at 40A every night. I have to think there is something different about our cars or our electrical service.
The one delivered with my car was a First Gen I know that, not sure what the second and third were, every one after that was a second gen UMC.
I do keep a spare just in case, the first failure scared me, as at the time, Public charging was almost non-existent.
But over the course of the UMC's, I did notice a direct correlation between how long they lasted, to the amperage I charge at.
While I have a HPWC now, I rarely use it. My car is a outside car, my garage, is mostly a "Warehouse" for my online business, so in order to get the HPWC cable to reach, half the car will be sticking out of the garage.
The UMC is more then enough, even when completly draining my battery. At 40 amps, I sustain about 235v on the UMC's circuit due to its run length to get all the way outside from my breaker box. 6 Awg at about 60 ft. As I lowered the amperage, so 39, 38, 37, 36 etc..., I noticed (Car under first year of ownership, UMC's are, at least according to Tesla, only under warranty for 1 year from purchase date of vehicle, or if ordered in the online store, 1 year from date of UMC purchase, no longer then that) that since the UMC was under warranty, experiment a bit with the amperage. Seems 32 was about the magic number. I usually charge much lower then this, 20 amps from 7pm to 7am is usually enough to give me a 90% charge on my 60kWh pack overnight, unless I get home much later.
I will add, UMC stays plugged in outside. It is in shade, and semi-protected from elements (rain) by a large roof over-hang.