Yeah, I hear ya. GFCI breakers don't even need a ground, but in the case of EVSE with self test of the ground circuit, there could be nuisance faults due to questionable conduit connections which would work fine for phase faults.
@Spartan86, as an FYI, the manual states:
Branch Circuit Conductors and Ground Wire
If installing for less than maximum power, refer to local electrical code to select correct conductors and ground wire size that are suitable for the chosen circuit breaker.
If installing for maximum power, use minimum 6 AWG, 90° C-rated copper wire for conductors.
This can be read to say the ground must also be 6 AWG, if you are setting it up at a 60 Amp feed. However, the heading calls out ground wire vs circuit conductor, so the 6 AWG may only relate to the phase conductors.
On the GFCI breaker bit: GFCI breakers rely on the neutral and ground bond being in place somewhere in the electrical system so that if something faults to ground some current will flow on that path, imbalancing the GFCI circuit and causing it to trip. So yeah, as you point out, the Wall Connector needs a solid ground connection so that it can test that the neutral/ground bond exists. Also, if you are running in metal conduit, having the conduit solidly grounded is critical since if a wire in the conduit melts you want it to fault to the conduit and immediately trip the overcurrent circuit breaker (which is not a GFCI in the case of a Wall Connector).
On the conductor sizing note: Yeah, I think that might be slightly confusing. There is no way Tesla is asking for a full 6 AWG ground. Typically above 10 gauge wiring the ground wires are allowed to be much smaller than the current carrying ones. In the NEC 10 gauge is good for up to a 60a circuit.
I also am totally confused by the requirement for 90C rated wire. This must be a quote from the latest generation Wall Connector manual? (I don't remember it being in the last gen one) Pretty much everything is 90c rated these days (Romex wire is even though code restricts you to the 60c rating, and generally all THHN is). But we are basically always limited to the 75c rating of the wire when connecting to residential circuit breakers which are pretty much universally limited to 75c. So I don't think the Tesla Wall Connector is saying its terminals are 90c rated, but perhaps instead they are saying that they just want to add an additional margin of safety by requesting 90c rated wire regardless?