Does any of the advice on appropriate tesla charger wire sizing change as a result of the 2020 updates to the code here?
Huh, interesting question to bring up, but I don't see anything there that would change this.
"Section 110.14(C)(2) covers separately installed pressure connectors such as power distribution blocks and recognizes the fact that many of them differ from circuit breaker terminals in that they are often rated higher than 75°C.
According to the new exception, a run of 90°C rated branch circuit conductors installed between 90°C rated power distribution blocks can be used at the maximum ampacity based on 90°C."
So it introduced some kind of specific exception case for things like "power distribution blocks", which could have lugs rated up to 90 degrees C. Residential consumer electrical equipment does not have that. Home breakers are only rated to 75 C and the connection lugs in EVSEs like the Tesla wall connector or others or regular outlets also are only rated to 75 C. So I still don't see any cases where you would get to use the 90 degree C rating of wire for these kinds of EV charging circuits.
The other thing about one of two ratings, I think still wouldn't change.
"210.19(A)(1) allows the larger of the following two values to be used for the final selection of the conductor:
Either 125% of the continuous load without any additional adjustment or correction factors,
OR
100% of the load (not 125% of it) after applying adjustment and correction factors."
It says the larger of the two. So let's say 48A charging. If you start at 48A and apply "adjustment and correction factors", which I'm not sure what all would go into that, you could see where that comes out. If that came to something bigger than 60, then I guess you're supposed to use that, but that sounds unlikely or a pretty rare case for some pretty harsh conditions. I think the +25% is already a pretty big oversize.
I feel like I'm in the kind of educated guess area on this, though, so not quite as confident. I am kind of getting the impression from this that the standard +25% that was being used before is the more cautious extra margin case, and this exception provision of correction factors sounds like a more big job industrial type of use case.