    Hi SureValla,

    I am not an electrician...
    The GE 100 AMP 240 looks like a possibility for you.
    Check with your electric code people, inspector, local electrician...

    The Square D Breaker enclosure is just an enclosure....
    From what it looks like you will have to buy the breakers and other switchgear to
    complete it.
    It will be much more expensive when you are done...

    Shawn
     
  3. miimura

    miimura Well-Known Member

    Joined:
    Aug 21, 2013
    Messages:
    5,548
    Location:
    Los Altos, CA
    You should talk to a local building inspector. The breaker panel solution may not be approved. On the other hand, if you want to be prepared for multiple Wall Connectors, the sub-panel solution is much better since you can have a separate breaker for each wall connector
     
  4. Daniellane

    Daniellane Active Member

    Joined:
    Aug 13, 2017
    Messages:
    2,244
    Location:
    Camas, Washington
    Just installed a second HPWC that was prewired when the first one wat installed last year..
    Both are now tied to just one100amp Breakerin the sub-panel
    There is a signal wire in a separate conduit for communication between the master and the slave HPWC.
    (Distributes available 80 amps to both cars when both are charging)
    Also installed a NEMA 14-50 outlet below the master as a backup in case of HPWC malfunction and to allow for driveway charging.
    #2 wire to both chargers. (Overkill)
    DCB126E4-56CA-4085-8B92-B72218884C99.jpeg
    169D4D03-FE3B-4240-AA0B-460058CE8C81.jpeg

    BFCF10AA-CE5F-4560-8C87-E2B3EDC56EED.jpeg
     
    • Informative x 1
    • Like x 1
    • Love x 1
  5. SureValla

    SureValla Member

    Joined:
    Mar 15, 2016
    Messages:
    626
    Location:
    Shelton, CT
    can you describe your original setup before the second HPWC?
     
  6. markb1

    markb1 Active Member

    Joined:
    Feb 17, 2012
    Messages:
    3,002
    Location:
    San Diego, CA
    Interesting. Tesla's own installation video routes the signal wire in the same conduit with the high-voltage wires. (Load Sharing - TESLA Wall Connector) I know it's typically not allowed run high-voltage and low-voltage together, but in this case, it seems that since both ends of the low voltage cable terminated in high-voltage enclosures, there's not much danger in the way Tesla does it. I'm no expert on what code says, though.
     
  7. miimura

    miimura Well-Known Member

    Joined:
    Aug 21, 2013
    Messages:
    5,548
    Location:
    Los Altos, CA
    Tesla also says that if you do run them in the same conduit, the insulation on the low voltage wire has to be rated for the higher voltage.
     
  8. Daniellane

    Daniellane Active Member

    Joined:
    Aug 13, 2017
    Messages:
    2,244
    Location:
    Camas, Washington
    Seemed unwise to run it in the same conduit, especially since it was already installed.
    Bought signal wire from my local Home Depot.
    Only 28 cents per foot for 18 gauge shielded 2 conductor. Under $17 for 60 feet. Only needed 30. Ran a spare in the same conduit for safety.
    [​IMG]
     
  9. Daniellane

    Daniellane Active Member

    Joined:
    Aug 13, 2017
    Messages:
    2,244
    Location:
    Camas, Washington
    Prior to adding the second HPWC everthing except signal conduit/wire and 2nd Wall Charger was there.
    There was a 2nd NEMA 14/50 where second Charger is now connected to the 50amp breaker with #2 wire.
    The NEMA 14/50 under the left Master HPWC was pre-wired but not connected.
    The 50 amp breaker which is now connected to the the NEMA 14/50 under the master HPWC (was connected to the removed NEMA 14/50 where the 2nd Charger is now)
    50amp breaker is switched off.
    Both Chargers are now bound together in the sub-panel and connected to the 100 amp Breaker.
    Had this inspected and informed him of our intentions regarding the 2nd Charger.
    One NEMA 14/50 was labeled “INACTIVE” at time of inspection.
    54A2073A-1920-4367-B7FB-A39F3AED9B2C.jpeg
     
    • Informative x 1
  10. doubleohwhat

    doubleohwhat Member

    Joined:
    Sep 1, 2016
    Messages:
    704
    Location:
    Alabama
    A lot of jurisdictions will allow 600v ethernet in the same conduit as electrical wiring. It's done often with solar installations. Just a note for anyone who comes across this thread in the future.
     
    • Like x 2

Share This Page

  • About Us

    Formed in 2006, Tesla Motors Club (TMC) was the first independent online Tesla community. Today it remains the largest and most dynamic community of Tesla enthusiasts. Learn more.
  • Do you value your experience at TMC? Consider becoming a Supporting Member of Tesla Motors Club. As a thank you for your contribution, you'll get nearly no ads in the Community and Groups sections. Additional perks are available depending on the level of contribution. Please visit the Account Upgrades page for more details.