If I had a 100A sub panel and wanted to use two HPWCs, these new ones would be the way to go with the additional data channel. I would install them each with their own 100A breakers and the data channel would enforce the 100A total draw as if they were on the same breaker. Well, technically they are on the same upstream breaker in the main panel. It's a win-win.... unless this is specifically disallowed by the install manual...
What do you know, I got it right. My main thinking for this approach - using a dedicated breaker for each Wall Connector instead of literally daisy chaining them - was that if one Wall Connector did crap out, it would be easy to shut off its breaker in the sub-panel and set the selector of the good one to use all the power.This would be a legal install, and the feeder sizing would consider this as a single load based on 220.62.
I'm still curious how much control the user has over the load sharing. Some users may want them to be sequential and some may want equal current. In a destination charging scenario, this could be important. If I was counting on the car being ready at a certain time, I wouldn't want someone else "stealing" priority.