eprosenx
Active Member
+1
My local inspector was not aware of an EV section in the code — I had to point it out to him. When I installed my WC with a 100-amp breaker he said it either had to be lockable or accessible and line-of-sight.
Hah, while this makes logical sense to me (either lockable OR line-of-sight) this is absolutely not how the code actually reads. It is funny how different jurisdictions just make up their own rules (sometimes more strict, sometimes less strict).
Here are the code sections:
So if you are OVER 60 amps on a circuit into your Wall Connector then a disconnecting means must be installed in a readily accessible location. You must be able to lock it in the off position. By my reading- A metal clip on the breaker that lets you lock the breaker "off" meets these needs (even if the breaker panel is elsewhere in the house - Readily Accessible to me just means you don't have to use ladders, etc...)
The other part of 625.43 applies if you are *more* than 150 volts to ground, but 240/120v split phase residential service will NEVER fall into this condition. This would apply if you had 277v going into a HPWC (which Tesla used to support, but they have taken it out of the manual).
In my case, I have a 60a breaker for my Wall Connector that I use to charge my M3. I triggered neither of these conditions, so I did not need a breaker lock-off device.
I have heard of jurisdictions requiring a disconnect switch right at the HPWC (like an AC unit requires), but this is NOT how I read the definition of "Readily Accessible" in Article 100. It seems silly to me. You don't generally have technicians accessing HPWC's all the time for maintenance like you do air conditioner units.