Thanks!The maximum amperage using THHN No. 6 wire (THHN wire being rated for 90C/194F), in this installation, would be determined by the temperature limit of the circuit breaker. A residential breaker will be rated for up to 60C (140F) or 75C (167F). Assuming the breaker is rated to 60C (140F) then a 55A limit would apply.
The Chargepoint EVSE can be set to a maximum of 50A. This is under the 55A limit and well within the 80% rule for EV charging for a 70A circuit. In this installation No. 6 THHN when used with a 70A (60C rated) breaker can support the Chargepoint EVSE set to operate at 50A.
Great! I get it and thought that might me the reasoning but never saw anyone ever acknowledge or set one up that way. I used a 60 amp to test but ordered a 70 amp breaker so I can push it to 50 amps which is the models limit. Every little bit helps. What surprized me was the price of the 70 amp versus the 60 amp Siemans .....6x the price at HD and Lo, but happened to find a new Siemans one for $30 elsewhere.I think all residential breakers are rated up to 75 degrees C. 6 gauge wire in conduit (THHN) is rated to 65A at 75 degrees C.
Your numbers aren't being done correctly, but I think you're accidentally coming out to the right answer.
So I think this is one of those odd examples where you do get to use the "round up rule" in NEC. The numbers look weird, but I think it's being followed correctly.
As I mentioned above, the limitation for 6 gauge THHN is 65A as the maximum rating limitation of the circuit. Continuous load can only be 80% of that, which is 52A. So that's where they get the 50A setting, which properly fits within it. But to have a 65A rated circuit, you generally can't find a breaker that is exactly 65A. So code allows a next sized up reasonably available breaker size, which would be 70 or 80. BUT THAT DOES NOT MAKE IT A 70 OR 80 AMP RATED CIRCUIT! It is still limited by the wire, so it's a 65A circuit.
All set up, activated and finally finished. Now just waiting for new EV if it ever shows up.