How can I tell if I have 220v or 240v installed?
I have an old dryer's plug (NEMA 10-30) with 30 amp breaker.
I have an old dryer's plug (NEMA 10-30) with 30 amp breaker.
You can install our site as a web app on your iOS device by utilizing the Add to Home Screen feature in Safari. Please see this thread for more details on this.
Note: This feature may not be available in some browsers.
How can I tell if I have 220v or 240v installed?
I have an old dryer's plug (NEMA 10-30) with 30 amp breaker.
That is definitely a 220V outlet.
That is definitely not a 220V outlet (it's a 240V outlet, split-phase 120V. With losses you might be seeing closer to 235V, but 220V seems kinda low)
That is definitely not a 220V outlet (it's a 240V outlet, split-phase 120V. With losses you might be seeing closer to 235V, but 220V seems kinda low)
Thank you both Chris TX and Max* for the answer. I replaced the 10-30 with a 14-50 plug, but still use the 30amp breaker. I dial down to charge at 26 amp.
Did you run a new ground wire? If not, that's not a legal/code compliant installation. And you need to dial down to 24A, not 26A. Even then, there's issues (common example given is a software update resets your charge rate to 40A, and you have a fire risk).Thank you both Chris TX and Max* for the answer. I replaced the 10-30 with a 14-50 plug, but still use the 30amp breaker. I dial down to charge at 26 amp.
Did you run a new ground wire? If not, that's not a legal/code compliant installation. And you need to dial down to 24A, not 26A. Even then, there's issues (common example given is a software update resets your charge rate to 40A, and you have a fire risk).
The ground wire is already there, it didn't connect with old dryer's plug, I connect the ground wire when I install the 14-50 plug.
How can I tell if I have 220v or 240v installed?
I have an old dryer's plug (NEMA 10-30) with 30 amp breaker.
I don't charge at home often, maybe once a week. I'm aware of the risk, my breaker tripped once due to the car reset back to 40A. Since then I'm very careful and check the charge amperage every time I charge at home, as long as the MS don't reset back to 40A during the charge, I should be okay. I will dial it down to 24A from now on.
- - - Updated - - -
The ground wire is already there, it didn't connect with old dryer's plug, I connect the ground wire when I install the 14-50 plug.
It sounds like he had a 4-wire installation, with 2 hots and a neutral to the 10-30, and an unconnected, separate ground. If so, that's sort of OK, but it should really be a 14-30. It's OK to install a 14-50 on a 40A circuit if a 40A appliance (like some ranges) is connected, but a 30A circuit is probably a no-no (especially since the UMC with a 14-50 isn't a 30A amp appliance). I'd try to scrounge up a 10-30 or 14-30 adapter, and use the matching outlet.Sounds like the old plug was mis-wired. It should have had a ground wire and two hots connected to it. The 14-50 adds a neutral wire in addition.
You really should put the 10-30 back and find a Tesla 10-30 adapter.
Sounds like the old plug was mis-wired. It should have had a ground wire and two hots connected to it. The 14-50 adds a neutral wire in addition.
You really should put the 10-30 back and find a Tesla 10-30 adapter.
It sounds like he had a 4-wire installation, with 2 hots and a neutral to the 10-30, and an unconnected, separate ground. If so, that's sort of OK, but it should really be a 14-30. It's OK to install a 14-50 on a 40A circuit if a 40A appliance (like some ranges) is connected, but a 30A circuit is probably a no-no (especially since the UMC with a 14-50 isn't a 30A amp appliance). I'd try to scrounge up a 10-30 or 14-30 adapter, and use the matching outlet.
It sounds like he had a 4-wire installation, with 2 hots and a neutral to the 10-30, and an unconnected, separate ground. If so, that's sort of OK, but it should really be a 14-30. It's OK to install a 14-50 on a 40A circuit if a 40A appliance (like some ranges) is connected, but a 30A circuit is probably a no-no (especially since the UMC with a 14-50 isn't a 30A amp appliance). I'd try to scrounge up a 10-30 or 14-30 adapter, and use the matching outlet.