Keep in mind 20% derating for continuous loads.
Derating applies to the circuit breakers after the transformer feeding the chargers. Power handling of the transformer itself would vary based on the cooling, i.e the ambient temperature and air circulation around its radiator.Does that apply to utility transformers? Several people on TMC have mentioned that you can actually exceed the transformer’s rating for brief periods of time.
I thought this thread was about the Frederick Supercharger.
Industrial customers are charged for the "surge" via a demand meter. This gets reset for every billing cycle.
I had gotten the 10 count off of the plans posted earlier in the thread. I don’t know where the 12 came from.
It's usually determined by the peak kW used in any period (often 5 or 15 minute measurement) of the billing cycle. Note, that is kW, not kWh. It's about the highest power draw, not the volume of energy used.That is not what I am asking. I'm asking how they define "surge", not how they measure it.
It's usually determined by the peak kW used in any period (often 5 or 15 minute measurement) of the billing cycle. Note, that is kW, not kWh. It's about the highest power draw, not the volume of energy used.
What do you mean "compared to"? There is a set price, $X/kW. If your peak is 3000 kW, then your demand charges will be 3000*X. If you want to see an example, below are the rates from a bill from Idaho Power and here's the document explaining the Large Service rates [pdf].Yes, of course it is the peak kW. But what is it compared to? I'm not asking for guesses. I thought maybe someone here would actually know how it is calculated.
That is not what I am asking. I'm asking how they define "surge", not how they measure it.
What do you mean "compared to"? There is a set price, $X/kW. If your peak is 3000 kW, then your demand charges will be 3000*X. If you want to see an example, below are the rates from a bill from Idaho Power and here's the document explaining the Large Service rates [pdf].
Springfield is 1000 kVA for 18 stalls or 55 kW per stall at full load (short of the 72 kW per stall equipment max). Most other Supercharger sites are sized similarly, with the utility transformer falling short of the site’s max theoretical output.
Frederick is 1000 kVA for 10 stalls or 111 kW per stall at full load, which is well in excess of the equipment’s capability to supply 72 kW per vehicle with all stalls in use. In my opinion, the only reason to size it that big is to accommodate a future expansion.
Keep in mind 20% derating for continuous loads
I assume the SC will be the traditional 150 KW units not 73 KW Urban chargers. so I would think we will be charging at a higher rate of charge. certainly better than Springfield. IF that was implied. We are still splitting between two pedestals though. I personally never see the high rates when I SC. I think 111 is the highest I have ever seen. 98 is more average or lower.
When I met the SC repairman at the Hagerstown site. He said the SC are simply the car's internal charge but a stack of them in Parallel. So this pedestal sharing will remain.
They just posted a good video on inside EV's detailing the Vegas V3 site. only a 2500 KVA feeding 24-V3 chargers as well as the destination chargers. We would be below 100 KW if the place filled up Also 4 pedestals seem to be shared on one SC cabinet. THe V3 Cabinets are a lot bigger so I can rule out Fredrick as a V3 site. The V3 dont have the side exhaust hood.
This applies for panels and wiring. Transformers are a grey area. technically I have seen them rated at 100% on most rating charts. I'm willing to bet the utilities probably over load them up to 50%. Also Since there transformers are liquid cooled I bet the ratings are much higher.
Did you mean 1,000 kW rather than 100 kW?
I'm not sure how liquid cooling makes a difference. Wouldn't that already be factored into the rating? While the internal is cooled by a liquid, the outside is still air cooled by convection. Or do they have fans on them? There's a power substation on East St in Frederick and it has a number of fans to blow on things.
East St Power
No the average per V3 charger at that site would only be about 100KW charge rate per car. Not bad. but not the 250 advertised.
I'm not sure how they would have listed a liquid cooled unit vs dry type. I would be pretty sure it could take the abuse of surges and high demand vs an air cooled unit. Otherwise the power companies wouldn't used them, is my reason to think so.
Baking vs boiling, overheating would more gradual with the oil filled???
The transformer has to be sealed in an enclosure to protect it from the elements. That inside is either an air space which does not conduct heat well or a liquid which does. I was not aware they used any transformers that were not liquid filled because of the cooling problems. Maybe we are not using the terms the same way. What are liquid and air cooled transformers to you?
I'm surprised they rate chargers at anything other than their peak rate which is what can and will happen. It doesn't happen long since the cars can only charge a higher currents over a smaller portion of the range/charge rate curve. Still, at some point there will be the max power draw which would be 250 kW for each pair of stalls or 125 kW on each stall. How long can a transformer built for 100 kW handle 125 kW? My area of expertise is much smaller and I treat max as absolute max. My designs have to worry about static discharges, not lightning. lol