In terms of price, then an earth electrode, clamp, buried box, cable etc will be around £40 or so About half this if a buried box isn't needed). If an additional length of rod is needed, then add a fiver. A Type B RCBO is now down to about £80, so the materials side of an earth electrode type installation would be around £120 or so. 99% of the time either a single rod, or an extension rod screwed on top, will get Ra down below 200 Ohms OK. The idea of placing additional rods 3m apart is a bit bonkers, really. If Ra can't be brought down to 200 Ohms or less with two rods screwed together (pretty rare) then just boring a post hole, filling it with Bentonite, and banging the rods back in will pretty much always do the job. There's a problem with skills fade when it comes to using earth electrodes, I suspect, as they are pretty unusual in modern domestic installations; nowadays most houses will have a protective earth provided on the incoming supply, either combined with neutral (a PEN) or as a separate conductor with a split concentric incoming cable.
The Type B RCBO replaces any RCD/MCB for the installation, and provides both earth fault protection and over-current protection.
For the matt-e solution, the materials cost looks to be a fair bit higher, but it saves a bit of work and makes the installation a bit simpler, from the electricians point of view. The question is really if you're prepared to pay a modest premium in order to make the job easier for the chap doing the installation.
Nothing to choose between the two options in terms of safety, although the earth electrode and Type B RCBO will respond a great deal faster if there's an earth leakage fault, no more than 30ms. The touch voltage protection device always takes more than 4s to trip, although whether this much longer trip time is important depends on the probability of someone standing next to the car and touching it at the same time that a fault occurs.
The Type B RCBO replaces any RCD/MCB for the installation, and provides both earth fault protection and over-current protection.
For the matt-e solution, the materials cost looks to be a fair bit higher, but it saves a bit of work and makes the installation a bit simpler, from the electricians point of view. The question is really if you're prepared to pay a modest premium in order to make the job easier for the chap doing the installation.
Nothing to choose between the two options in terms of safety, although the earth electrode and Type B RCBO will respond a great deal faster if there's an earth leakage fault, no more than 30ms. The touch voltage protection device always takes more than 4s to trip, although whether this much longer trip time is important depends on the probability of someone standing next to the car and touching it at the same time that a fault occurs.