That you cannot do. There is an exception for running a 40a breaker on a 50a outlet and a 25a breaker on a 30a outlet because outlets don't exist for those amperages. Otherwise the outlet has to match the breaker. However, you can install a 20a outlet, then buy the proper adapter from Tesla.
It's kind of a combination of the table in 210.24 and the table in 210.21 (b) (3).I'd love to see the section of NEC code that says this (honestly).
It's kind of a combination of the table in 210.24 and the table in 210.21 (b) (3).
https://www.google.com/url?sa=t&rct=j&q=&esrc=s&source=web&cd=1&cad=rja&uact=8&ved=0ahUKEwjpuouW4_vaAhUH7GMKHX72DhUQFggpMAA&url=https://www.legrand.us/~/media/files/ews/installation%20guidelines%20for%20receptacles%20on%20small%20appliance%20branch%20circuits.ashx&usg=AOvVaw2YT4uRHfHMEWJ-eRSlEifg
Why is it OK to use a 50 A receptacle on a 40 A circuit?
The wording of these says that the outlet type cannot be less than the circuit breaker rating. The 210.21.(b)(3) does specifically show that for 40A circuits, 40 or 50A outlets are allowed. Since there is no 40 amp outlet type, it has to go upward to the 50.
I don't see the problem with a 15 amp outlet on a 20 amp branch. You might have 4 or 5 outlets on that circuit so it makes sense to me to have a higher amperage circuit. The important thing is to use 12ga wire on that 20 amp circuit and not 14ga like you could on a 15 amp circuit.Thanks for the link.... shaking my head.... you can use a 15 amp outlet on a 20 amp branch and you can use a 40 amp outlet on a 50 amp branch... wow. Goes against everything I know electrical..... :-/
I could in theory melt my 15 or 40 amp outlet before tripping the breaker.I don't see the problem with a 15 amp outlet on a 20 amp branch. You might have 4 or 5 outlets on that circuit so it makes sense to me to have a higher amperage circuit. The important thing is to use 12ga wire on that 20 amp circuit and not 14ga like you could on a 15 amp circuit.
There are no 40 amp outlets, so your second example is moot. The common example from this thread is using a 32A EVSE on a 50 amp NEMA 6-50 outlet and a 40 amp breaker. That is actually how the installation manuals for those EVSE are written. Personally, I would use 6ga wire so that the circuit could be upgraded to 50 amps with ample wire headroom.
How are you going to melt your 15 amp outlet with a 15 amp device? 20 amp outlets are mechanically different with one prong perpendicular.I could in theory melt my 15 or 40 amp outlet before tripping the breaker.
No, that is specifically not allowed. See what it said above. The outlet type has to be at least as high as the circuit rating. So your example of a 40 amp outlet on a 50 amp branch circuit is forbidden. The example in the tables is the other way around, where it's a 40 amp branch circuit, but the outlet is 50. So think it through, the breaker will trip sooner, which is what you want with the wires being smaller.Thanks for the link.... shaking my head.... [...] and you can use a 40 amp outlet on a 50 amp branch...
You have to know where the 100.42A load is distributed. I would guess 30A dryer, 10A washer, 10A dishwasher, electric or gas range + lights etc. If you are to have all of them turned on, you may not want to exceed 20A as suggested but in reality most people won't have all those turned on while charging (especially midnight)
@Lewisball Regarding your situation, I also have a 125A main panel, so my situation is similar. Furnace is gas and water heater is gas, so those aren't in there, but the big electrical loads are A/C, clothes dryer, and oven. As someone mentioned, a 240V 20A circuit is fairly OK for overnight charging, so just getting a 6-20 outlet type and buying the Tesla 6-20 adapter would work pretty well for a decent charging rate.
But...30 or 40 amp might be pretty useful sometimes. Here is what I would consult with your electrician about. When doing a load calculation, there is an official provision called "non-concurrent loads". It means if two loads are not going to be used at the same time, they obviously don't BOTH need to be added to the total. You can add the bigger of the two. So in other words, if I have a 50A circuit for my oven, and want to have a 30A circuit to charge the car, I will set the car to only charge after midnight and not use the oven after midnight. So you don't need to count 50 + 30 into the load calculation. You can just use the 50, and it will be one or the other in use at a time. Or you could pick the clothes dryer versus car charging. Or you could count it the other way, with the car circuit as the bigger one--50A circuit for the car OR 30A for the dryer. You only count the 50. That would increase your house's total by 20, which he did say was acceptable.
So ask him to check the load calculation again if you consider the car charging circuit as a nighttime only load offset versus one of the big daytime only loads. You can probably get something a little bigger because it wouldn't be an entirely new amount added to the total.
Is there a way to set the model 3 to only charge during certain hours?
I have had 2 inspectors in 2 counties (Los Angeles and Orange counties) tell me that a 14-50 needs a 50A breaker UNLESS it is something that is fixed in place (like a Range) or is hardwired, I have installed at least 12 of these and the first one was on 8/3 with a 40A breaker, I was forced to change it out to a 14-30 with a 30A breaker for it to pass inspection, this was an inspector for Long Beach in LA county, I asked the next inspector in Los Alamitos, Orange county and he gave me the same info, this is just my experience but both inspectors had the same interpretation of the code.It's kind of a combination of the table in 210.24 and the table in 210.21 (b) (3).
https://www.google.com/url?sa=t&rct=j&q=&esrc=s&source=web&cd=1&cad=rja&uact=8&ved=0ahUKEwjpuouW4_vaAhUH7GMKHX72DhUQFggpMAA&url=https://www.legrand.us/~/media/files/ews/installation%20guidelines%20for%20receptacles%20on%20small%20appliance%20branch%20circuits.ashx&usg=AOvVaw2YT4uRHfHMEWJ-eRSlEifg
Why is it OK to use a 50 A receptacle on a 40 A circuit?
The wording of these says that the outlet type cannot be less than the circuit breaker rating. The 210.21.(b)(3) does specifically show that for 40A circuits, 40 or 50A outlets are allowed. Since there is no 40 amp outlet type, it has to go upward to the 50.
Very helpful! Thanks.
There are two parts to this:I have had 2 inspectors in 2 counties (Los Angeles and Orange counties) tell me that a 14-50 needs a 50A breaker UNLESS it is something that is fixed in place (like a Range) or is hardwired,
That doesn't even make any sense. If it is hardwired, then by definition it is not a device that plugs into a receptacle, so a 14-50 outlet wouldn't even be in the discussion.a 14-50 needs a 50A breaker UNLESS it [...] is hardwired,
My whole quote was this.There are two parts to this:
(1) Yes, I think the wording in the code for this does give an example of a range, and I think it may mention "fixed in place". Some inspectors take that fixed part a little more loosely. A range usually isn't "fixed in place", and the frequent application to EVSEs are wall units that do hang with a mounting bracket, so that would usually qualify as fixed, but if you are showing that it's for a 30-some amp EVSE, they will sometimes allow that.
(2) What the heck? Are you sure you heard this right from two inspectors?
That doesn't even make any sense. If it is hardwired, then by definition it is not a device that plugs into a receptacle, so a 14-50 outlet wouldn't even be in the discussion.
It depends on what kind of wire and conduit you used between the outlet and the breaker box. If you left Romex exposed, it won't pass. If you used 6ga THHN in metal conduit, it will pass. Got a picture?So, I don't know what I'm doing, and this is what I did: 4 "blade" NEMA running four feet, outlet to breaker. 240V with 50a breaker off 6 gauge wire. Charging model 3 through mobile connector. Will have inspector sign off work in a couple weeks. Am I cool?
So, I don't know what I'm doing, and this is what I did: 4 "blade" NEMA running four feet, outlet to breaker. 240V with 50a breaker off 6 gauge wire. Charging model 3 through mobile connector. Will have inspector sign off work in a couple weeks. Am I cool?