I probably should have explained it better but by "2 input" I mean input from 1 pole, 3 phases down to transformer, and the second input, from the other pole, also 3 phase down to transformer but I hope others understood what I meant.
Yes (and if you do that, it would defeat the whole idea leaving the feeder connected between the poles as well, because then you can't isolate the two sections and the substation).
This isn't some special deal for Superchargers by the way, it's a pretty standard arrangement for padmount/kiosk substations.
Ok
![Thinking face :thinking: 🤔](https://cdn.jsdelivr.net/joypixels/assets/8.0/png/unicode/64/1f914.png)
, where from your reply do I start because I think you/we are getting confused. It also appears to me you are getting, how shall I put it nicely? Hmm, "assertive" or even "angry". But I could be wrong.
Now l suggest we start with somethings we maybe able to agree to.
So we have a Supercharger substation that needs to be connected to the 3 phases, or the 3 wires on top of those poles, of the 11kV (11,000 volts) part of the grid. So far I am just trying to make it easier for as many members as possible on this forum to follow in this discussion.
Now in this case of the Tesla Superchargers in Taree I have shown photos of 2 existing poles with cables lying on the ground obviously I think waiting for for their connection.
Now here comes the confusion to this whole saga IMHO. I think you do "not" need 2 poles to send 3 simple phase wires down to a substation transformer in normal circumstances. From my experiences with substation transformers, I have one sitting on my land supplying my engineering factory, 1 pole with 3 wires are sent underground to send to the substation. Hell I even have photos taken today of the pole out the front of my factory. No special 2 pole setup just 1 pole with 3 phases or wires.
A simple join to the 3 phases it appears to me through "circuit breakers" and wires run down the conduit underground to Substation:
And here is the "padmount/kiosk substation" next to my factory:
So simple IMO, 3 phases or 3 wire feed connection to a transformer.
But the Tesla site will have I think 6 wire feed.
So tell us what you think is going on that we need a 6 wire connection to a simple substation and you already know what I think it might be.