My reading of the NEC says that for 75˚C and 90˚C rated insulations, #8 copper wire is approved for a 50 Amp circuit. See Table 310.15(B)(16) from the 2014 NEC below. On the other hand, I agree with you; for lower Voltage drops and more thermal margin, when I have had 50 Amp circuits installed, I have requested #6 wire be used.
Also, you can see that #3 copper wire is sufficient for a 100 Amp circuit; I have installed two HPWC's, and two CS-90's; in each location, I have requested the use of #2 copper because it is often cheaper and more available than the less common #3, but more importantly, because it provides extra margin for the install.
View attachment 40495
BTW, Table 310.15(B)(2)(a) does provide derating factors for ambient temperatures other than 30˚C, 86˚F, and for a 40˚C, 104˚F, garage and for the most common 75˚C insulation, #6 copper would be required.
According to the NEC the conductors need to be selected not only based on temperature rating of the conductor
INSULATION but also based on the temperature rating of the
TERMINATIONS. Refer to NEC Section 110.14 (C)(1)
Electrical Connections-Temperature Limitations-Equipment Provisions. This section essentially states that regardless the temperature rating of the insulation, the conductors must be sized based on the temperature ratings of the terminations. The default rating of the terminations for 600V and below circuits less than 100A is 60˚C. So unless all of the terminations of all of the components of the circuit (panelboard breaker, Nema 14-50 wall outlet, Tesla plug adapter, tesla plug on UMC adapter side) have terminations rated higher then 60˚C, the proper conductor sizing must be based on 60˚C column of the table 310.15(B)(16) as appropriately modified by 310.15(B)(7).
The problem is that a lot of electricians as well as electircal engineers are confused with this requirement and size conductors improperly. I participated in writing Cable Size Selection Guide for a major corporation which design and build power plants, and experienced this confusion among many engineers I delt with first hand.
The subject is addtionally clouded by the fact that majority of the low voltage breakers rated less than 100A are nowadays have terminations rated 75˚C. Based on this a lot of people jump the gun and size conductors based on 75˚C, forgetting that other components of the circuit may be rated 60˚C, and in fact, according to the NEC must be assumed to be rated at 60˚C unless listed and marked otherwise. The most common NEMA 14-50 outlet, Leviton 279-C00 linked below has rating of 60˚C (30˚C temperature rise over 30˚C ambient)
http://www.leviton.com/OA_HTML/ProductDetail.jsp?partnumber=279-C00§ion=42418&minisite=10251
I am willing to bet that majority of the overheating adapters are linked with the wiring installation using undersized conductors. This could be further exacerbated by the improperly tightened connections, improperly seated Tesla adapter, etc.
Tesla is doing the right thing providing redundant ways (software + replacing the adapters) to fix the potential problems with the equipment installation which has nothing to do with their design, because explaining these intricacies to a wider audience is a loosing battle.
- - - Updated - - -
This is incorrect. #8 AWG is good to 50 amps when used at 75 degree rating. If you use type NM cable, which requires you use the 60 degree column, you are correct in that #6 is needed. However, #8 AWG in conduit is just fine for 50A feeding a 14-50 outlet. (NEC table 310.15(B)(16))
Sorry, Flasher, you are wrong on this one, see my post #93. The proper minimum size of the conductors to use for 14-50 outlet, regardles of the rating of insulation is #6AWG. It must be based on the lowest temperature rating of the
TERMINATIONS, which is commonly 60˚C for NEMA 14-50 outlet.
This demonstrates the problem with confusion about the proper sizing of the conductors based on temperature rating of the terminations. I have read quite a few of your posts which are excellent, but you unfortunately just wrong on this one. Given my experience with fellow engineers and electricians, I am surprised that adapter overheating is not a more common that it seems to be.