A permit is different than an inspection. The permit doesn't do much. The inspection may possibly get someone knowledgeable to catch mistakes.Doesn't getting a permit eliminate the worry?
You can install our site as a web app on your iOS device by utilizing the Add to Home Screen feature in Safari. Please see this thread for more details on this.
Note: This feature may not be available in some browsers.
A permit is different than an inspection. The permit doesn't do much. The inspection may possibly get someone knowledgeable to catch mistakes.Doesn't getting a permit eliminate the worry?
That's part of the process here. Isn't that normal for everywhere in the US?A permit is different than an inspection. The permit doesn't do much. The inspection may possibly get someone knowledgeable to catch mistakes.
No. It depends on how rebellious/independent your state or city are. I live in Idaho, which still has a lot of background history and attitude that comes from the frontier, pioneer, homesteader, leave me the f&%$ alone, don't want no government, kind of stuff. So a homeowner is allowed to do many kinds of upgrades and improvements to his house without needing permits or inspections.That's part of the process here. Isn't that normal for everywhere in the US?
Yeah, I guess here in IL we're on the other side of that kind of "freedom". At least up here in the Chicago suburbs.No. It depends on how rebellious/independent your state or city are. I live in Idaho, which still has a lot of background history and attitude that comes from the frontier, pioneer, homesteader, leave me the f&%$ alone, don't want no government, kind of stuff. So a homeowner is allowed to do many kinds of upgrades and improvements to his house without needing permits or inspections.
It eliminates some legal and liability worries, but if it's still done wrong and burns your house down, that'll be cold comfort.Doesn't getting a permit eliminate the worry?
Wall connector option: You need a 60-amp standard breaker ($15) and wire rated at a 60-amps. #6 THHN in a conduit is needed. The connector is currently about $475 and your car will charge at a maximum rate of 48-amps. Total cost of this option is about $490 plus the wire.
Electrician coming tomorrow morning for 240V NEMA 14-50 outlet installation , he said he will use 6awg and 60 amp breaker and Bryant .
Please suggest any other things to take care. Thank you
Get an electrician, not the fool you chose.
That’s a 50A breaker which is the correct one for a 14-50 receptacle.
If you substitute a TWC for the 14-50, that breaker and wire should be compliant.Electrician coming tomorrow morning for 240V NEMA 14-50 outlet installation , he said he will use 6awg and 60 amp breaker and Bryant .
Please suggest any other things to take care. Thank you
He just installed this for 240v outlet
Sort of. The amp level is right, except that code does have that irritating requirement that breakers for EV charging outlets must be GFCI type, which this isn't.That’s a 50A breaker which is the correct one for a 14-50 receptacle.
Right, and that would also be the correct breaker type for a wall connector since hard wired devices don't require GFCI breakers.If you substitute a TWC for the 14-50, that breaker and wire should be compliant.
Sorry, I did not get this , substitute a TWC means ??If you substitute a TWC for the 14-50, that breaker and wire should be compliant.
Nvm , got it , you mean Tesla wall connector , now I spent for electrician and mobile connector and the reason going for it is I drive very less , was using regular 110v charging for last 6 months as I drive very less , work from homeSorry, I did not get this , substitute a TWC means ??
He is builder contracted electrician, he has done TWC earlier and mentioned never installed 240v outlet for EV , so the confusionGet an electrician, not the fool you chose.
This is a little subjective, because the words "should be" don't have a definite meaning. I would say they should be, so I consider it true. It can cause confusion and problems if people don't, so I recommend that the better and preferred way should be just doing it as a 50A circuit.Fwiw, folks pretty regularly claim a 14-50 receptacle should be paired with a 50a breaker. This is not true.
You are talking about "must be", and you're correct that it is not a requirement.Nothing wrong with using a 14-50 receptacle on a 40 amp breaker So long as wiring as wiring matches the breaker. That would be fine for a mobile charger, as one example.
Right, that does depend on NEC version adoption in your state.similarly, a GFCI breaker, while defined by current code, may not be required.
Let's be honest--that actually is very unusual statistically. 43 states in the U.S. are on NEC 2017 or 2020. That is the vast majority of states that do have this requirement. So yes, it is unusual to not have it now (see map of NEC versions below).as our code compliance spec is something like 2014 code version. That’s not all that unusual.