So I need to tell him to use 50amp breaker ? It’s all new for me , pls suggestA 60 amp breaker is not allowed to be used with a 50 amp receptacle.
You really shouldn't NEED to tell him. It should be a 50 amp GFCI breaker.So I need to tell him to use 50amp breaker ? It’s all new for me , pls suggest
Thanks , it’s a new home and builder contracted electrician, he came to fix the non working switch, and offered me installation by seeing my car, he said he will get all materials and install that outlet for me in garage beside breaker panel for $350, when asked he told the details like 60amp, 6 awg etcYou really shouldn't NEED to tell him. It should be a 50 amp GFCI breaker.
Good point. Going the route of a Tesla Wall Connector will provide you 48 amps vs a mobile connector at 32 amps.Usually purchasing, installing the Tesla Wall Connector instead of installing a 14-50 receptacle and purchasing the Tesla Mobile Connector is the better option.
Only if the circuit wiring is rated for 60 amps and has a 60 amp circuit breaker. If the circuit wiring and circuit breaker is rated for 50 amps then the maximum charging amperage when using the Tesla Wall Connector is 40 amps, not 48 amps. (That would still be 25% higher amperage than the 32 amp maximum when using the Tesla Mobile Connector with the 14-50 power plug and 14-50 receptacle.)Good point. Going the route of a Tesla Wall Connector will provide you 48 amps vs a mobile connector at 32 amps.
Run.Thanks , it’s a new home and builder contracted electrician, he came to fix the non working switch, and offered me installation by seeing my car, he said he will get all materials and install that outlet for me in garage beside breaker panel for $350, when asked he told the details like 60amp, 6 awg etc
So you don‘t get lost in the details:
NEMA 14-50 outlet option: needs a 50-amp GFCI breaker ($150) and wire rated at 50-amps or greater. #6 Romex (NM-B) wire is fine as it is rated at 55-amps. The outlet needs to be a Bryant or Hubbell outlet ($80). And of course the mobile connector ($230). Your car will charge at a maximum rate of 32-amps (Mobile Connector limit). Add some sort of cable management system ($35) and you are at about $495 plus the wire.
Wall connector option: You need a 60-amp standard breaker ($15) and wire rated at a 60-amps. #6 THHN in a conduit is needed. The connector is currently about $475 and your car will charge at a maximum rate of 48-amps. Total cost of this option is about $490 plus the wire.
Unless you have some other need for the 14-50, you should consider going with the wall connector.
Recently built a house with 3 wall connectors. It was discussed throughout the build for 60 on each. Found out they were only 50 so set up each charger for 40amps. I'm thinking they may had did a load test, but other than the AC everything is gas.If the circuit wiring and circuit breaker is rated for 50 amps then the maximum charging amperage when using the Tesla Wall Connector is 40 amps, not 48 amps. (That would still be 25% higher amperage than the 32 amp maximum when using the Tesla Mobile Connector with the 14-50 power plug and 14-50 receptacle.)
Doesn't getting a permit eliminate the worry?It's probably a state by state thing. Here in Illinois it doesn't take much to call yourself an electrician. The non-sense I've seen - Golly. It's expensive, but in this state the union forces a level of knowledge such that theres often a considerable difference in expertise.
That said, I've used plenty of electricians that didn't know some aspects of code. None have had a problem with me saying "I'm sure you're right, but I'll spend the money to get XYZ. Ymmv.