No actually they don't range from 110-120v. The spec is 120v plus or minus a percentage.
ANSI C84.1 Service Voltage Limits
Ø Range A minimum voltage is 95% of nominal voltage
Ø Range A maximum voltage is 105% of nominal voltage
Notice that is 5% above or below. Nothing about 110V being OK. In case I need to do the math for you:
114V is 5% below nominal
110V is over 8% below nominal.
If you see voltage dropping to 108v (which is 10% below nominal) you are either experiencing a brownout or your wiring is substandard.
as a counter example to your low voltage if I measure an outlet in my house I see between 119v and 125v depending on the time of day/weather/what I have turned on in the house. I commonly see 121V to 123V more so than either end of that range.
We are talking about the same thing, and it isn't necessarily a brownout or substandard wiring. I think if you google it you find that there are plenty of references to the common outlet voltage range being "110V - 120V", and many common household devices explicitly claim to operate in that range for a reason. it's a combination of the variance around 120V plus voltage drops due to resistance if the outlet is wired far from the breaker, or from extension cords.
I agree 108V is a bit low, but it was 112V without current. The plug in question is at the very bottom floor of the parking garage at my work I suspect as far from the breaker as possible.