Thanks. That is some good information. My house is 2850 sq ft with an unfinished basement. So if I had to go to 60 amps, would it still be recommended to run 3 awg?
Also for the calculator, will the Wattage spec that each field requires be found on an information label on each appliance?
Sorry, forgot to answer the Wattage question.
Typically yes (although I found my stove was labelled incorrectly -- very rare and odd). I'm not sure what an inspector will officially ask for, but for standard appliances that use plugs (i.e. that can be changed), the maximum of the appliance rating or 80% of the circuit rating might be more appropriate. For hard-wired appliances (like A/C, hot water tanks), you can certainly use the rating of the unit as they cannot be "swapped" by the customer without due consideration. [I'm stretching a bit here in this paragraph as I don't know for sure.]
Most appliances will give a maximum current rating (e.g. 12 A) and an operating voltage (220-240V). Sometimes, there will be a peak current rating (typically for compressor startup) and a continuous load rating. For load calculations, you can probably get away with the continuous current rating (although the circuit wiring and breaker must be rated for the peak current).
You always need to use 240V for the load calculation (it says so in the code, section 8-100).
If you cannot find the rating of the appliance, then use the breaker rating (which will be slightly higher than most appliances), or if you want to, use 80% of the breaker rating, as that is officially the maximum load you are supposed to have on the circuit.
(And as a reminder for anyone who needs a quick refresher:
Power (P, in Watts) = Voltage (V, in Volts) * Current (I, in Amps)
P = VI
e.g.:
Voltage 240 Volts
Current: 12 Amps
Power = 240 * 12 = 2880 Watts
)
A reminder, I'm not a certified electrician or an expert -- just done lots of reading recently on this. And the inspector's interpretation of the code may vary (and their's is the only one that matters in the end).